Solar Guppy - All Things Solar Forum

It is currently Sun Apr 28, 2024 7:39 am GMT EthGMT

All times are UTC - 5 hours [ DST ]




Post new topic Reply to topic  [ 4 posts ] 
Author Message
 Post subject: SMA: Grounding: NEC
PostPosted: Sun Jun 01, 2003 11:16 am GMT EstGMT 
Offline
Fish Eggs
Fish Eggs

Joined: Sun Jun 01, 2003 1:01 am GMT EstGMT
Posts: 7
Location: San Jose, CA USA
After much analysis, I decided to use Sunnyboys and now have my electrical permit.

The City of San Jose put a note on my drawing to make sure I comply with sec. 690-41 of the National Electric Code. This requires that one side of the PVs be grounded. From the manual, it looks like the Sunny Boy requires both + and - PV inputs to be isolated from ground.

How is sec. 690-41 interpreted in a Sunny Boy system? Do I tell them that I have a "3-wire" system, with the third wire being the ground? I don't think so - I believe that by 3-wire they mean a "center-tapped" string. Or are we using the "other methods" exception?

Also, sec. 690-5 requires GFDI devices. It appears that this is built into the Sunny Boy. Has anyone gotten an electrical inspector to accept this?

Jerry


Top
 Profile  
 
 Post subject: Grounding: NEC
PostPosted: Sun Jun 01, 2003 11:46 am GMT EstGMT 
Offline
Goldfish
Goldfish

Joined: Fri Jan 31, 2003 2:01 am GMT EstGMT
Posts: 97
Location: Long Island, NY
Hi,

With the Sunnyboy, the negative PV (groundED conductor) is connected (bonded) inside of the inverter to ground (groundING conductor) thru the GFDI circuitry that is built into the inverter.

The PV frame and mounts need a separate groundING wire.

[ June 01, 2003: Message edited by: Ron Schroeder ]


Top
 Profile  
 
 Post subject: Grounding: NEC
PostPosted: Mon Jun 02, 2003 1:48 pm GMT EndGMT 
Offline
Fish Eggs
Fish Eggs

Joined: Sun Jun 01, 2003 1:01 am GMT EstGMT
Posts: 7
Location: San Jose, CA USA
Thanks, Ron. If the PV negative is BONDed inside, then it all makes sense and I know what I SHALL do to pass the inspection. By the way, I can tell from your careful use of words that you've been reading the NEC!

Jerry


Top
 Profile  
 
 Post subject: Grounding: NEC
PostPosted: Mon Jun 02, 2003 8:48 pm GMT EndGMT 
Offline
Goldfish
Goldfish

Joined: Fri Jan 31, 2003 2:01 am GMT EstGMT
Posts: 97
Location: Long Island, NY
Hi Jerry,

You SHALL have a good time with PV. [img]images/smiles/icon_wink.gif[/img]


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Powered by phpBB © 2000 - 2020 phpBB Group

phpBB SEO

© SGT 2002 - 2020 Solar Guppy