The only sw4048's that meet UL REQUIRE the GTI ... I'm 100% sure of this. No SW4048 installations without GTI's are UL1741 listed, I was with Xantrex when all this went down and I know first hand what happened. Based on your firmware ( 4.10 ), I would say you have a pre 2001 unit, that's NOT certified for gridtie, you need updated firmware ( 4.20 ) and the GTI units for you installation
Hear is the manuals on the required GTI
http://www.xantrex.com/web/id/115/p/doc ... roduct.aspAnd quoted from the manual, page 7
http://www.xantrex.com/web/id/605/docserve.aspxQuote:
All new SW Series II units (manufactured since December of 2001) are
equipped to allow the GTI to be installed in the field. The SW Series II inverter is
Certified to UL1741 for off grid and backup power applications. The SW can be
connected to the grid as a battery charger; however, it is NOT approved to use the
SELL feature (net meter) without the GTI accessory. The GTI carries all necessary
approvals and markings to allow a safety inspector to approve the installation for net
metering.