The FX80 are charge controllers, I was refereing to the inverters, Outback are 3.6kW max each and only 120V, since you running both 120/240 ( AC ) the only option is the WX-6048 inverter. The inverter will handle on demand turning on/off the generator.
For Charge Controllers I would suggest the WX one, I am biased as its partly my design working, its also convection cooled ( no fans ) and best in class Mppt performance
Your looking at a very, very large system, you should really look at a pacakged XW system, 12kw ( pair of XW-6048's, probably 3-4 XW mppt charge controllers, nice thing about the XW system is you can get the BOS box that simplifys all the AC and DC breakers and interconnects ... but warning, this is a VERY advanced project you concidering and NOT something a first time user should do.
Expense wise, I'd say your looking at probably near 100K when you add in the batterys, generator, all the balance of system parts .. unless local power is 1.00 watt you much better off with grid power and again, you can't control the renters, no matter what you think you can do, they will find some way to exceed the systems ability and you better have a backup plan when the inverters shutdown due to,
no fuel for the generator
Batterys die from abuse
inverters trip on overloads
ect ect
It is a doable project, but very expensive, very technical to get it all integrated and almost 100% for sure not cost effective for return on investment. You might also be VERY concerned about theft, a 100K system is a 30 year mexican salary for the taking when your not around
|