 Post subject: A question about grounding
PostPosted: Fri Apr 03, 2009 8:08 am GMT ErdGMT 
Offline
Catfish
Catfish
User avatar

Joined: Fri Sep 29, 2006 10:57 pm GMT EthGMT
Posts: 43
I am wondering what the consensus is on using conduit as the ground instead of running a ground wire through the conduit. From what I've read, the conduit really is better than a wire, at least up to a few hundred feet, BUT, if the conduit isn't put together properly then there is a major problem.

So will the local inspectors here in Florida allow the conduit to be used as the ground? It seems that the NEC allows it, but then I've read that in some places the local people require a grounding wire.

Also, if a grounding wire is needed, which is correct: that it needs a ground equal to the largest wire in the conduit, even if that wire is oversized, or that it needs at most a 6awg wire?


Top
 Profile  
 
 Post subject: Re: A question about grounding
PostPosted: Fri Apr 03, 2009 12:25 pm GMT ErdGMT 
Offline
Guppy
Guppy
User avatar

Joined: Mon Mar 20, 2006 7:58 pm GMT EthGMT
Posts: 214
Location: pittsburgh
conduit may present discontinuity and high resistance points and is really only meant to physically guide and protect the wiring.


Top
 Profile  
 
 Post subject: Re: A question about grounding
PostPosted: Fri Apr 03, 2009 1:23 pm GMT ErdGMT 
Offline
Catfish
Catfish
User avatar

Joined: Fri Sep 29, 2006 10:57 pm GMT EthGMT
Posts: 43
Yes, it can be bad if the conduit isn't connected properly. It can get incredibly technical. From what I've read, some connect the grounding nut by tightening the conduit and holding the nut, but it seems that it is required to hand tighten the nut and then tighten it at least 1/4 turn more, to scratch the paint off the surface of any metal box. There should be some way though to test if the conduit is acting effectively as the ground, but the test instrument probably costs $1000.

I started wondering because I read: http://www.steelconduit.org/pdf/TechTal ... unding.pdf


Top
 Profile  
 
 Post subject: Re: A question about grounding
PostPosted: Fri Apr 03, 2009 8:36 pm GMT ErdGMT 
Offline
Red Cobra Delta Guppy
Red Cobra Delta Guppy
User avatar

Joined: Sun Jun 02, 2002 1:01 am GMT EndGMT
Posts: 1159
Location: Lakeland Florida
I have never heard of, or done personally or see in the wild inspected electrical that used conduit for ground. It can easily be pulled part without any indcation that this has happened. For your Bartow job, pull a green wire the same size as the PV runs and you will have no issues with Polk County inspectors on that aspect of the installation


Top
 Profile  
 
 Post subject: Re: A question about grounding
PostPosted: Sun Apr 05, 2009 3:44 pm GMT EthGMT 
Offline
Catfish
Catfish
User avatar

Joined: Fri Sep 29, 2006 10:57 pm GMT EthGMT
Posts: 43
Yes, I figured that no matter having a grounding wire must add to the safety. It seems too that the ground wire should be insulated instead of bare if it is in conduit.

I did end up wishing I would have listened closer to Larry at G&G Electric when he said to step up a size or two for conduit, but having 1 1/2" conduit running in the garage seemed so much more industrial, so I stayed with the 1" conduit.

I was just wondering too if you had the name of the electrician who oversaw your installation there in Lakeland. I was real happy with your suggestion of Robert Haug for the P.E. There are a few last details that I wanted to make sure were OK and Larry is pretty busy at the moment.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
cron
Powered by phpBB © 2000 - 2020 phpBB Group

phpBB SEO

© SGT 2002 - 2020 Solar Guppy