Author:  nigtomdaw [ Wed Aug 08, 2007 6:54 pm GMT EthGMT ]
Post subject:  Xantrex: SG Please Help

Please look at my question on Xanrex.com re the new XW60 MPPT . If I cant ground my -ve batt terminal if I get a new XW do I have to separately ground my C40s and LA arrestors, can u see the point Im trying to raise ? :shock:

Author:  niel [ Wed Aug 08, 2007 9:04 pm GMT EthGMT ]
Post subject: 

could you copy it and paste it here for all to see? this also makes it easier on sg.

Author:  nigtomdaw [ Wed Aug 08, 2007 9:17 pm GMT EthGMT ]
Post subject: 

Ok Niel as requested but SG is a big boy,


PS Dont give me a hard time on NAWS I like it lots

Author:  Solar Guppy [ Wed Aug 08, 2007 9:23 pm GMT EthGMT ]
Post subject: 

NEC regs require solar panels on a roof to be ground fault protected. In the WX-MPPT60-150, this is done by the ground to PV Minus bond being made thru the WX charger, which has a Ground Fault detection circuit.

If another ground to PV Minus bond is made else where in the "system", it will disable this required protection

Now on the C60, the ground connection is NOT bonded to the PV Minus or Battery Minus, ground is for the MOV's protection. Also any other equipement ground would be similar, Ground is NOT PV or Battery Minus ... it only becomes bonded at one place.

In an older system, that would be at the battery terminal, now its at the WX charger.

Hope this helps

Author:  nigtomdaw [ Wed Aug 08, 2007 9:28 pm GMT EthGMT ]
Post subject: 

Post deleted by Mod as its redundant ........

Question has been answered, move the ground to PV minus bond from the battery to the new charger, one wire gets moved

Author:  nigtomdaw [ Wed Apr 02, 2008 9:49 pm GMT EndGMT ]
Post subject: 

The XW has a jumper included to disable the GFP for people like me who have a system wired as per Xantrex SW spec inverters with a DC250 disconnect junction box with a -ve ground bond and a Xantrex tech.

This is usefull for systems not covered by NEC ( North American ) installations that do not have the GFP requirements

( edited by MOD to deleted off topic comments )

Author:  nigtomdaw [ Thu Apr 03, 2008 6:04 pm GMT ErdGMT ]
Post subject: 

Can I view deleted off topic comments SG

Author:  Solar Guppy [ Thu Apr 03, 2008 6:28 pm GMT ErdGMT ]
Post subject: 

I don't see that feature with this forum sofware

Author:  nigtomdaw [ Sun Apr 06, 2008 8:10 pm GMT EthGMT ]
Post subject: 

OK i see, thanks for thant :D