 Post subject: Xantrex: XW-6048 setup Need Some Help Please
PostPosted: Sun Aug 03, 2008 5:35 pm GMT ErdGMT 
Offline
Fish Eggs
Fish Eggs
User avatar

Joined: Sat Aug 02, 2008 4:28 pm GMT EndGMT
Posts: 7
Location: Arizona
I am a newbie but have read tons about it so I decided to jump in.

I have a new system of a xw6048 and 24 of the roller s-450 batteries and a 20kw 100 amp generator.

The set up is approximately 3 weeks old and everyhting was working fine and then all of a sudden it wont charge past two light and then just goes to bypass on the generator.

I have the xw controller and auto generator start module. Why would it say it's charging but won't charge more than 30%

I haven't changed any of the setting from when it was working fine. Any help would be appreciated

Thanks


Top
 Profile  
 
 Post subject:
PostPosted: Sun Aug 03, 2008 6:31 pm GMT ErdGMT 
Offline
Red Cobra Delta Guppy
Red Cobra Delta Guppy
User avatar

Joined: Sun Jun 02, 2002 1:01 am GMT EndGMT
Posts: 1159
Location: Lakeland Florida
Do you have the SCP control panel? it would show error codes to help understand whats going on

Also, you maybe overloading the inverter or generator? when charging what is the amps displayed?

When it goes to bypass, is it still charging, IE showing amps on the display?, if your charging at max amps you can't then load the output as well, 6kW is combined of charging/inverting

As for why now issues, well its probably just starting to have to charge the batterys, I didn't lookup the specs, but sound like a huge battery pak, whats the specs?


Top
 Profile  
 
 Post subject:
PostPosted: Sun Aug 03, 2008 9:19 pm GMT ErdGMT 
Offline
Fish Eggs
Fish Eggs
User avatar

Joined: Sat Aug 02, 2008 4:28 pm GMT EndGMT
Posts: 7
Location: Arizona
Solar Guppy wrote:
Do you have the SCP control panel? it would show error codes to help understand whats going on


Yes I have the SPC controller and I checked the log and there was nothing there

Quote:
Also, you maybe overloading the inverter or generator? when charging what is the amps displayed?


When it does come on with the charging light on it will fluxuate between 89 to 100 amps

Quote:
When it goes to bypass, is it still charging, IE showing amps on the display?, if your charging at max amps you can't then load the output as well, 6kW is combined of charging/inverting


No. the light on the kw comes on and the read out has all 0's

Quote:
As for why now issues, well its probably just starting to have to charge the batterys, I didn't lookup the specs, but sound like a huge battery pak, whats the specs


It is a 1050 ah battery pak and sorry I spelt it wrong it's Rolls brand, and when we first installed them it went from fully loaded to 1 light and the controller started the generator and in a couple hours fully charged again.

We are running the whole house on this as a off grid system and I will be needing advice on the solar panel which I will post in the right section tomorrow.

Again thank you for helping and if there is something else I should check let me know and I will get it posted asap[/quote]


Top
 Profile  
 
 Post subject:
PostPosted: Sun Aug 03, 2008 10:09 pm GMT ErdGMT 
Offline
Red Cobra Delta Guppy
Red Cobra Delta Guppy
User avatar

Joined: Sun Jun 02, 2002 1:01 am GMT EndGMT
Posts: 1159
Location: Lakeland Florida
I'd double check the setup using the SCP to check the battery voltages and charging modes ...

I have never use the generator input or setting it up ... My XW-6048 is grid based.

I seems like its running more like my setup, that being seeing the AC input and going into bypass as mine unit does normally.

So, check the charging ( I use 2 stage with no float ), make sure your battery aH is setup correctly and battery type. Verify that the SCP reported voltage is the real battery voltage with a DVM


Top
 Profile  
 
 Post subject:
PostPosted: Mon Aug 04, 2008 11:14 am GMT EthGMT 
Offline
Fish Eggs
Fish Eggs
User avatar

Joined: Sat Aug 02, 2008 4:28 pm GMT EndGMT
Posts: 7
Location: Arizona
Here are all my settings, you would know better then me.

Main Settings

Inverter Enabled
Search Mode Disabled
Grid Support Disabled
Charger Enabled
Force Chg is Blank
Equalize Disabled
Mode Operating

Inverter Settings

Low Batt Cut out 44.0V
LBCO Delay 10sec
High Batt cut out 70.0V
Search Watts 50w
Search Delay 2sec

AC Settings gen on AC2

AC2 Breaker 60.0amp
Low V 80.0v
high v 138.0v
lo freq 55hz
hi freq 65hz

Generator Support Enabled
Gen Amp 48.0Amp

Charging Details

Battery type Flooded (my batties are not listed)
Batt Capacity 1050 ah
Max Charge 100%
Charge Rate 2stgnofloat
battery temp warm
recharge volts 48.0v
absorb time 180min
chrg block start 12:00am
chrg block stop 12:00am

Auto Gen Start Settings

Generator Mode Automatic
Mode Operating

cfg trigger settings

Start DCV 30 sec 50.0v
Stop Float Enabled
Load Disabled
srt load 15.0a
stop load 7.0a


SCP displays with generator running and charge light on

Battery flux between 92.2a to 100a 52.2v
batt level stays the same at 2 lights so about 35%
load 933w

AC2 119v 6100w

Hopefully this gives you a bit more insight.

Thanks again so much


Top
 Profile  
 
 Post subject:
PostPosted: Mon Aug 04, 2008 11:34 am GMT EthGMT 
Offline
Red Cobra Delta Guppy
Red Cobra Delta Guppy
User avatar

Joined: Sun Jun 02, 2002 1:01 am GMT EndGMT
Posts: 1159
Location: Lakeland Florida
OK, so whats the problem, its charging 100 amps which is the maximum,

You have a 1kw load, which is what is causing the 90-100 amp variation

what happens next?, does the voltage ever make it to the Bulk/Absorb transistion ( 57.6 V without a BTS )

It will take about 5-8 hours @ 100 amps to take a battery @ 30% SOC to 80% SOC as an estimate for a 1000ah pack. Batterys are about 80% efficient, so to go from near delpleted to near full charge would take over 12+ hours at 100 amps

I notice the absorb is only 3 hours, that maybe much to short to completely charge the batteries of that size ( aH ), you should check the manufactures suggested charging rates and time.

Please explain in detail what is you issue as I'm not clear at this point beyond having 3 lights instead of 5 shoowing what this issue is.

The lights arer nothing more than a voltage based state of charge ( compenstated when you have a BTS ).

Under load, the lights may indicated a state of charge lower than actual and if you don't have a BTS ( you really need one for your system ) the voltage is effected by battery tempature so that will skew the charge status

Also the Generator must be 240V, I assume it is based on the amps setting and the Volts setting is for each L1/L2 of the AC2 input

Also

http://www.xantrex.com/web/id/1871/docserve.aspx

is the users manual, page 34 ( 2-11 ) & 35 ( 2-12 ) explain how to use the SCP to see the Status of the unit, most helpful for you would be to monitor ( figure 2-6 ) the XW6048 home screen. It showes amps and states to indicated exactly wht the XW is doing


Last edited by Solar Guppy on Mon Aug 04, 2008 2:10 pm GMT EthGMT, edited 1 time in total.

Top
 Profile  
 
 Post subject:
PostPosted: Mon Aug 04, 2008 12:42 pm GMT EthGMT 
Offline
Fish Eggs
Fish Eggs
User avatar

Joined: Sat Aug 02, 2008 4:28 pm GMT EndGMT
Posts: 7
Location: Arizona
Now I understand, and thank you for the link to the manual. I looked through everything i had recieved from the dealer and do not have that manual which is explaining the things I needed to know.

I will go through it thoughly and thanks again


Top
 Profile  
 
 Post subject:
PostPosted: Mon Aug 04, 2008 1:31 pm GMT EthGMT 
Offline
Fish Eggs
Fish Eggs
User avatar

Joined: Sat Aug 02, 2008 4:28 pm GMT EndGMT
Posts: 7
Location: Arizona
Just got off the phone with my dealer where I bought the stuff and he said oh I took it out of the box to show someone else and I guess I forgot to put it back.


Top
 Profile  
 
 Post subject:
PostPosted: Mon Aug 04, 2008 2:08 pm GMT EthGMT 
Offline
Red Cobra Delta Guppy
Red Cobra Delta Guppy
User avatar

Joined: Sun Jun 02, 2002 1:01 am GMT EndGMT
Posts: 1159
Location: Lakeland Florida
You can download all the XW manuals from the Xantrex/xw website

For a beginner, you have a huge system ... when you figure out what's happening, please post a follow-up for others to see what was happening


Top
 Profile  
 
 Post subject:
PostPosted: Mon Aug 04, 2008 2:57 pm GMT EthGMT 
Offline
Fish Eggs
Fish Eggs
User avatar

Joined: Sat Aug 02, 2008 4:28 pm GMT EndGMT
Posts: 7
Location: Arizona
will do my friend


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 11 posts ]  Go to page 1, 2  Next

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 6 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
cron
Powered by phpBB © 2000 - 2020 phpBB Group

phpBB SEO

© SGT 2002 - 2020 Solar Guppy