The key to module matching is matching within each string. PV cells are essentially current sources with current proportional to insolation. As an example of matching, if four modules are connected in series and three of the modules produce 6 amperes while the fourth module produces 5.5 amperes, the four module string will only produce 5.5 amperes -- dominated by the weakest current. The key is to wire strings of four each of which produce about the same amount of current. (If one is using a SunnyBoy with one 24 modules string, the current is set by the weakest module and you can't do a thing about it.)
As for how to match, I did the following:
I took one module, exposed it to full sunlight (no clouds) and measured short-circuit current with a DMM. I then took and second module and placed it is the same postion exactly as the first and measured its short-circuit current, recording the result. I repeated the test on all 48 of my modules. After every six modules were tested, I returned the first module to the testing positon to correct for any changes in insolation. By the way, one must be very careful to avoid things like reflections off your shirt which will mess up your measurements. Given this data, I matched up the modules in groups of four where each module in a group is matched as closely as possible. Then I installed the PV modules wiring each circuit from matched sets.
Gordon
|