A quick check of the NEC reveals the following:

#10 RHW-2 OR USE-2 (without the outer covering):
3/4" EMT or PVC Sch 40 = 6 conductors
1" EMT or PVC Sch 40 = 10 conductors


#10 THHN:
3/4" EMT = 10
1" EMT = 16

3/4" PVC Sch 40 = 9
1" PVC Sch 40 = 15

You should also have a ground wire (#10) in the conduit.
If THHN is used, it must be terminated in an enclosure.


Top
 Profile  
 
 Post subject:
PostPosted: Mon Nov 12, 2007 4:34 pm GMT EthGMT 
Offline
Catfish
Catfish

Joined: Sat Oct 20, 2007 12:34 pm GMT EthGMT
Posts: 38
Location: So. Orange County, CA
well after my making a fairly big stink about it, my installer agreed to pull an additional home run so that I will not need to combine strings on a single 10AWG circuit.

Thanks for all the feedback from everyone on this...hearing the strong opinions from this community was a big part of why I decided to push hard to have it redone correctly.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 17 posts ]  Go to page Previous  1, 2

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
cron
Powered by phpBB © 2000 - 2020 phpBB Group

phpBB SEO

© SGT 2002 - 2020 Solar Guppy