Hi gang,
Well, after 2 years with 30 PhotoWatt PW1000 (100Watt) Panels, I'm noticing that the backside electrical connections are coming loose. Symptom is low power output, caused by loose connections.
On the back of each panel is a weatherproof plastic box. Within the box is a 7-screw electrical junction strip, used to jumper the panel for 12V/24V operation, and for external electrical connections. The terminal strip uses 6x32 screws to clamp wires or solderless terminals.
When I put the panels up 2 years ago, I torqued all the wires to 12 in-lbs.
Now (August 2003), I find that many of the screws have loosened, resulting in high-resistance connections (sometimes open circuits!). In one case, I could see pitting caused by sparks on the barrier-strip.
Probable culprit? Repeated hot-cold cycles. From day to night, the barrier strips vary over 100 degrees F. Bit by bit, the thermal expansion/contraction forces the screw to slowly untwist.
Looks like every year I should climb my roof, unmount each panel, and re-tighten each screw. My installation has some 200+ such screws.
I'll probably retrofit with lockwashers and perhaps anerobic loctite threadlock. I wonder if there's an electrically conductive loctite?
-Cliff
|