Minnow |
|
Joined: Mon Aug 06, 2007 3:27 pm GMT EthGMT Posts: 10 Location: Palmer, Alaska
|
Neil,
We ended up moving the controllers. Tried the split ferrite cores but no improvement. Never even tried shielding. By moving the controllers to the generator shack we got several benefits-
-less than 10' of cable to the batteries
-generator building is skinned in metal, so it's somewhat of a faraday cage
-further from the tower/antennas, which is where the noise was getting into the radios
The sites that have never given us a problem will probably not get moved.
|
|