This is about calculating the maximum current for NEC 690.8
I relied on
http://solar.wiseowlnetworks.us/Solar-Math.html for doing the calculations of the maximum "PV Source Current Circuit Current." Now I'm wondering if this is in fact correct.
So, for calculating the maximum "PV Source Current Circuit Current" for NEC 690.8 (A) (1) is it strictly Isc *1.25 (125%)? And then the second 1.25 factor (690.8 (B)(1)) is your standard safety factor when sizing conductors.
Or is it as stated on that solar math website, that you use NEC Table 690.7 to calculate the maximum "PV Source Current Circuit Current" for the low temperature (up to 1.25 depending on the lowest temperature) and then multiply that by 1.25 (125%) because of "its solar" as stated on that website?
But Table 690.7 states it is the "Voltage Correction Factor" not the Current Correction Factor.
I'm really asking because if it that website is wrong then my PV circuit breakers may be calculated wrong too.
The Isc of the Sharp 224U1F is 8.33A. I then multiplied that by 1.14 (because the record low for Bartow was 18°F and in NEC Table 690.7 that equates to 1.14) to get 9.4962 and then multiplied that by 1.25 to get 11.87025. So I purchased a 12A breaker for each PV circuit.
But if it is 8.33 * 1.25 * 1.25 that equals 13.0156, which means you need a 15A breaker for each PV circuit.
I don't know how critical this is, or if it could be allowed to "slip through" by the local inspectors. I know they never said anything when they reviewed my detailed plan I submitted for getting the permit. By calculating with the "Maximum Power Current" you get 11.96875, which is still less than the 12A breaker for the PV circuit. Wouldn't you want the breaker to trip any time the current is greater than the "Maximum Power Current" not the "Short Circuit Current" anyway?