The instructions on how to do the installation are available upon request, you just need to call Schneider Electric (Xantrax) and ask for them to send you a copy in your E-Mail. My understanding is the Kit will also come with a set of instructions but I wanted to familiarize myself with the procedure before the kit arrived.
FYI After the "Lock-Out and Tag-Out Procedure" the instructions read-
"To remove existing capacitors and hardware: 1. Remove the GT inverter's front cover which is located just above the wiring disconnect box. 2. Remove the existing capacitors (see Figure 1): -For UL-01 units, remove capacitor C3 from the AC interconnect board using a pair of channel lock pliers and a side-to-side twisting motion (do not pry up and down as this may cause PCB damage). Be careful not to damage the surrounding components (e.g. fuse holder and fuse). Trim any long leads that remain on the board and remove any debris and loose adhesive. Do not attempt to remove intact adhesive as this may cause damage to the board. -For UL-05 units, remove capacitors C1 and C6 using the same techniques described for the UL-01 unit above. 3. Remove PCB mounting screw on the left side of the AC interconnect board and disgard. See Figure 2."
It continues on to describe the disconnection of the L1 and L2 black and red AC wires from the AC interconnect board (on the right of the display screen, to the lower right of the AC fuse on UL-01 and below the fuse on UL-05 models). You connect them to the supplied PCB and connect the leads on the new PCB to the original connection locations of L1 and L2 on the AC interconnect board. Then you mount the new PCB to the existing AC interconnect board using the hardware kit they are supposed to supply.
|